Question 1022 of 344 · NICET Fire Alarm Systems Level II
Which circuit types may share a cable with PLFA conductors under NFPA 70?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1022
- D: Class 2 and 3 circuits with insulation equal to PLFA
Explanation
Class 2 and Class 3 conductors may be in the same cable as PLFA conductors if their insulation is at least that required for the PLFA circuits. Class 1, NPLFA, and power circuits must be kept separate.
More questions: Installation
- 1023What does NFPA 70 require for the branch circuit supplying a fire alarm control unit?
- 1024Where must the location of the fire alarm branch circuit disconnecting means be documented?
- 1025NFPA 70 requires fire alarm circuits to be identified at terminal and junction locations. What is the purpose?
- 1026How must exposed fire alarm cables above a suspended ceiling be supported under NFPA 70?
- 1027What must be done with the accessible portion of abandoned fire alarm cable?
- 1028Cable ties used to secure fire alarm cables in a plenum space must have what property?