NFPA 70 requires fire alarm circuits to be identified at terminal and junction locations. What is the purpose?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1025
- C: To prevent accidental interference during testing and servicing
Explanation
Identification at terminals and junctions prevents other trades or technicians from disturbing fire alarm circuits by mistake during testing and servicing of other systems.