Question 1024 of 344 · NICET Fire Alarm Systems Level II
Where must the location of the fire alarm branch circuit disconnecting means be documented?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1024
- B: At the fire alarm control unit
Explanation
The circuit disconnect location must be permanently identified at the control unit so that technicians can find it. The disconnect itself carries red identification and the FIRE ALARM CIRCUIT label.
More questions: Installation
- 1025NFPA 70 requires fire alarm circuits to be identified at terminal and junction locations. What is the purpose?
- 1026How must exposed fire alarm cables above a suspended ceiling be supported under NFPA 70?
- 1027What must be done with the accessible portion of abandoned fire alarm cable?
- 1028Cable ties used to secure fire alarm cables in a plenum space must have what property?
- 1029What is the minimum conductor size permitted for NPLFA circuits?
- 1030What is the maximum overcurrent protection for 18 AWG NPLFA conductors?