How must exposed fire alarm cables above a suspended ceiling be supported under NFPA 70?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1026
- B: By the building structure
Explanation
Cables must be supported by the building structure using hardware such as straps or hangers. Ceiling support wires and grids may not be used, and PLFA cables may not be strapped to the exterior of raceways as a means of support.