Question 1042 of 344 · NICET Fire Alarm Systems Level II
What does NFPA 72 require for the primary power source of a fire alarm system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1042
- B: A dedicated branch circuit from commercial light and power
Explanation
The primary supply is normally a dedicated branch circuit of a commercial light and power source. Engine driven generators and similar sources are permitted only in specific approved arrangements.
More questions: Installation
- 1043Which mechanical protection is required for the fire alarm branch circuit disconnecting means?
- 1044Where can conductors of a Class A NAC be allowed to share a single conduit for the outgoing and return run without violating the separation rule?
- 1045Where must a smoke detector used for elevator recall be located?
- 1046Which kind of detector is normally used to initiate elevator power shutdown (shunt trip) before sprinklers discharge in the machine room?
- 1047For elevator shunt trip, how close must the heat detector be to each sprinkler head it protects?
- 1048Which signal should a sprinkler waterflow switch with retard delay produce, and what is the maximum delay allowed before the alarm is initiated?