During rough-in, the technician finds that a duct now sits where a smoke detector is shown on the approved drawing. What is the correct action?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1040
- A: Report it and get an approved revision first
Explanation
Field changes to an approved design must go through the designer and, where required, the AHJ. Relocating a device can affect spacing and coverage, so the change is documented and approved before installation.