Question 1041 of 344 · NICET Fire Alarm Systems Level II
Which item must be installed so that the fire alarm system wiring does not degrade over time and terminations stay reliable?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1041
- A: Neat and workmanlike wiring per NFPA 70
Explanation
Fire alarm equipment must be installed in a neat and workmanlike manner, and wiring must follow NFPA 70. Poor workmanship is a frequent cause of later ground faults and opens.
More questions: Installation
- 1042What does NFPA 72 require for the primary power source of a fire alarm system?
- 1043Which mechanical protection is required for the fire alarm branch circuit disconnecting means?
- 1044Where can conductors of a Class A NAC be allowed to share a single conduit for the outgoing and return run without violating the separation rule?
- 1045Where must a smoke detector used for elevator recall be located?
- 1046Which kind of detector is normally used to initiate elevator power shutdown (shunt trip) before sprinklers discharge in the machine room?
- 1047For elevator shunt trip, how close must the heat detector be to each sprinkler head it protects?