Question 1045 of 344 · NICET Fire Alarm Systems Level II
Where must a smoke detector used for elevator recall be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1045
- B: Elevator lobbies, the machine room, and the hoistway if required
Explanation
Elevator recall detectors are installed in elevator lobbies, the elevator machine room, and in the hoistway when required, such as where sprinklers are installed there. They initiate Phase I recall per ASME A17.1.