Question 1044 of 344 · NICET Fire Alarm Systems Level II

Where can conductors of a Class A NAC be allowed to share a single conduit for the outgoing and return run without violating the separation rule?

Exactly one answer is correct.

Show solution

Correct answer to question 1044

  • D: On short drops to a single device, within the exception

Explanation

The separation rule has a limited exception: the conductors may run together for up to 10 ft where they enter or leave a device or control unit enclosure, such as the drop to an individual device. Outside that exception, the outgoing and return paths must be separated.