Where can conductors of a Class A NAC be allowed to share a single conduit for the outgoing and return run without violating the separation rule?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1044
- D: On short drops to a single device, within the exception
Explanation
The separation rule has a limited exception: the conductors may run together for up to 10 ft where they enter or leave a device or control unit enclosure, such as the drop to an individual device. Outside that exception, the outgoing and return paths must be separated.