Question 1090 of 344 · NICET Fire Alarm Systems Level II
What wiring method is used to connect a fire alarm system to a sprinkler valve tamper switch?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1090
- D: A supervisory circuit that signals when the valve moves
Explanation
Valve supervisory switches report a supervisory signal, distinct from alarm and trouble. The signal must initiate within two revolutions of the handwheel or one fifth of the travel distance and restore only when the valve is fully open.
More questions: Installation
- 1091A valve supervisory switch must initiate a signal within what amount of valve movement?
- 1092A combination system shares a control unit for fire alarm and security functions. What must the installer make sure of?
- 1093What is the purpose of an end of line resistor on a conventional Class B initiating device circuit?
- 1094Where must the end of line resistor of a Class B circuit be installed?
- 1095When wiring to an initiating device, why must the circuit conductor be broken at each terminal rather than looped (T-tapped) on a conventional Class B circuit?