Question 1094 of 344 · NICET Fire Alarm Systems Level II
Where must the end of line resistor of a Class B circuit be installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1094
- B: At the last device on the circuit
Explanation
The end of line device must be at the far end of the circuit. If it were placed at the panel, the field wiring would not be supervised and an open would go undetected.
More questions: Installation
- 1095When wiring to an initiating device, why must the circuit conductor be broken at each terminal rather than looped (T-tapped) on a conventional Class B circuit?
- 1096Which type of short circuit isolator placement allows a Class X SLC to keep operating after a single short?
- 1097Which records must be completed for a new system and given to the owner after acceptance?
- 1098In a corridor not more than 20 ft wide, how far apart may visible appliances be spaced under the corridor rule of NFPA 72 (2022)?
- 1099A wall mounted visible appliance must cover a 20 ft by 20 ft room by itself. What minimum effective intensity does the wall mounted room table require?
- 1100A 40 ft by 40 ft room will be covered by one wall mounted strobe. What minimum effective intensity does the wall mounted room table require?