Question 1093 of 344 · NICET Fire Alarm Systems Level II
What is the purpose of an end of line resistor on a conventional Class B initiating device circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1093
- B: To let the panel supervise for opens
Explanation
The panel monitors a small current through the end of line resistor. An open stops that current and produces trouble, while an alarm device placed across the circuit draws more current and produces alarm.
More questions: Installation
- 1094Where must the end of line resistor of a Class B circuit be installed?
- 1095When wiring to an initiating device, why must the circuit conductor be broken at each terminal rather than looped (T-tapped) on a conventional Class B circuit?
- 1096Which type of short circuit isolator placement allows a Class X SLC to keep operating after a single short?
- 1097Which records must be completed for a new system and given to the owner after acceptance?
- 1098In a corridor not more than 20 ft wide, how far apart may visible appliances be spaced under the corridor rule of NFPA 72 (2022)?