Question 1092 of 344 · NICET Fire Alarm Systems Level II
A combination system shares a control unit for fire alarm and security functions. What must the installer make sure of?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1092
- B: Fire signals have priority and are not interfered with
Explanation
In combination systems, fire alarm signals must have priority over other signals, and faults in non-fire equipment must not interfere with required fire alarm functions.
More questions: Installation
- 1093What is the purpose of an end of line resistor on a conventional Class B initiating device circuit?
- 1094Where must the end of line resistor of a Class B circuit be installed?
- 1095When wiring to an initiating device, why must the circuit conductor be broken at each terminal rather than looped (T-tapped) on a conventional Class B circuit?
- 1096Which type of short circuit isolator placement allows a Class X SLC to keep operating after a single short?
- 1097Which records must be completed for a new system and given to the owner after acceptance?
- 1098In a corridor not more than 20 ft wide, how far apart may visible appliances be spaced under the corridor rule of NFPA 72 (2022)?