Question 1096 of 344 · NICET Fire Alarm Systems Level II
Which type of short circuit isolator placement allows a Class X SLC to keep operating after a single short?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1096
- C: Isolators between segments, so only the faulted one is lost
Explanation
Isolators on both sides of a section separate a short from the rest of the loop. With the redundant return path, all devices outside the isolated section continue to communicate.
More questions: Installation
- 1097Which records must be completed for a new system and given to the owner after acceptance?
- 1098In a corridor not more than 20 ft wide, how far apart may visible appliances be spaced under the corridor rule of NFPA 72 (2022)?
- 1099A wall mounted visible appliance must cover a 20 ft by 20 ft room by itself. What minimum effective intensity does the wall mounted room table require?
- 1100A 40 ft by 40 ft room will be covered by one wall mounted strobe. What minimum effective intensity does the wall mounted room table require?
- 1101Which control function is commonly wired from a fire alarm relay to release magnetically held smoke doors?
- 1102Where must the relay or control module that operates an emergency control function be located?