Question 1095 of 344 · NICET Fire Alarm Systems Level II
When wiring to an initiating device, why must the circuit conductor be broken at each terminal rather than looped (T-tapped) on a conventional Class B circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1095
- C: So a removed device or loose wire shows trouble
Explanation
Conductors must be broken at device terminals (no looping a continuous wire under one screw). Then a disconnected device or loose conductor interrupts the supervision current and is reported, which T-taps would hide.