A wall mounted visible appliance must cover a 20 ft by 20 ft room by itself. What minimum effective intensity does the wall mounted room table require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1099
- C: 15 cd
Explanation
For a 20 ft by 20 ft room with a single wall mounted appliance, the room spacing table requires 15 cd. A 28 ft by 28 ft room needs 30 cd and a 40 ft by 40 ft room needs 60 cd with one appliance.
More questions: Installation
- 1100A 40 ft by 40 ft room will be covered by one wall mounted strobe. What minimum effective intensity does the wall mounted room table require?
- 1101Which control function is commonly wired from a fire alarm relay to release magnetically held smoke doors?
- 1102Where must the relay or control module that operates an emergency control function be located?
- 1103How are HVAC fan shutdown circuits typically installed when they are not monitored for integrity?
- 1104What must happen to the fire alarm system when an emergency control function interface relay fails?
- 1105Which interface must be provided so that elevators are not recalled to a floor where the lobby detector is in alarm?