A technician bypasses a zone for testing and forgets to restore it. What risk does this create?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2027
- D: A real fire in that zone would not be reported
Explanation
Every disabled point is an impairment. At the end of testing, all bypassed, disabled, or silenced points must be restored and the system returned to normal, with the panel showing no abnormal conditions.
More questions: Maintenance
- 2028The control unit shows a ground fault trouble. What is the most efficient first step to locate it?
- 2029A technician measures resistance from one conductor of a disconnected circuit to a known building ground. Which reading suggests a ground fault?
- 2030With field wiring disconnected and the far end of a Class B IDC open (EOL removed), what reading between the two conductors indicates a short?
- 2031A Class B IDC with a 4.7 kilohm EOL resistor reads infinite resistance at the panel terminals with field wiring removed. What does this indicate?
- 2032A 24 VDC NAC with a 2.2 kilohm EOL is checked with the panel in normal (supervisory) condition. Which measurement confirms the EOL is in place?
- 2033Why are notification appliances on a supervised NAC polarized (diode blocked)?