When replacing a failed addressable smoke detector with a new one, what must the technician verify?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2074
- A: It is listed as compatible and set to the right address
Explanation
Replacement devices must be listed for use with the control unit and set to the same address and type. Incompatible devices may not communicate or may not meet the listing.
More questions: Maintenance