Question 2073 of 344 · NICET Fire Alarm Systems Level II
A dual path communicator loses its cellular path but keeps its IP path. What must the system do?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2073
- D: Report a trouble signal for the failed path
Explanation
Loss of any communication path must be annunciated as trouble at the protected premises and the supervising station, within the specified time, so it can be repaired before the second path fails.
More questions: Maintenance
- 2074When replacing a failed addressable smoke detector with a new one, what must the technician verify?
- 2075Which document should be used to confirm the correct operation of each input and output during testing?
- 2076A technician finds several corroded terminals in an outdoor junction box on an IDC. Which fault is most likely to result?
- 2077An SLC with 60 addressable devices has a ground fault. The technician lifts the field wiring at device 30 and the ground fault trouble clears. Where is the fault?
- 2078A ground fault trouble appears only during heavy rain and clears in dry weather. What is the most likely cause?
- 2079A Class A IDC shows an open circuit trouble, yet every device on it still alarms when tested. Why?