Question 2075 of 344 · NICET Fire Alarm Systems Level II
Which document should be used to confirm the correct operation of each input and output during testing?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2075
- B: The sequence of operations (input/output matrix)
Explanation
The sequence of operations, often in matrix form, defines what each initiating device must cause, such as notification, elevator recall, door release, and HVAC shutdown. Testing verifies each of those outputs.
More questions: Maintenance
- 2076A technician finds several corroded terminals in an outdoor junction box on an IDC. Which fault is most likely to result?
- 2077An SLC with 60 addressable devices has a ground fault. The technician lifts the field wiring at device 30 and the ground fault trouble clears. Where is the fault?
- 2078A ground fault trouble appears only during heavy rain and clears in dry weather. What is the most likely cause?
- 2079A Class A IDC shows an open circuit trouble, yet every device on it still alarms when tested. Why?
- 2080A short circuit occurs on a Class A SLC that has isolator modules between groups of devices. What is the expected result?
- 2081A NAC has 12 strobes. The technician removes the EOL resistor and measures resistance across the disconnected field conductors with the meter leads in normal polarity. The reading is a few ohms. What does it indicate?