A room is 40 ft by 64 ft with a 20 ft smooth ceiling. Heat detectors are listed for 50 ft (adjusted spacing 32 ft). What is the minimum detector count on a square grid?

Exactly one answer is correct.

Show solution

Correct answer to question 3012

  • B: 4

Explanation

40 / 32 = 1.25, round up to 2 rows. 64 / 32 = 2 columns. 2 x 2 = 4 detectors. The layout is checked so no point is farther than 0.7 x 32 = 22.4 ft from a detector.