A projected beam detector is listed for a maximum beam length of 330 ft and a width of 60 ft. How far from the side wall may the beam be placed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3013
- D: Up to 30 ft, half the width
Explanation
Beam detectors are laid out like spot detectors along their length: the distance to a side wall must not exceed half the listed spacing width. With 60 ft listed width, the maximum is 30 ft.
More questions: Submittal Preparation and System Layout
- 3014A 20 ft by 30 ft room has a 10 ft ceiling and will use one wall mounted strobe in the middle of the long wall. Which room size must be used to pick the candela?
- 3015A room is 30 ft by 30 ft with one wall mounted strobe. What minimum effective intensity applies?
- 3016A 24 V battery set must support a standby load of 0.32 A for 24 h and an alarm load of 3.6 A for 5 min. Apply the 1.25 aging correction factor of NFPA 72 (2022/2025). What capacity is required?
- 3017An emergency voice/alarm communication system has a standby load of 1.1 A and an alarm load of 6.0 A. It needs 24 h standby and 15 min of alarm, with the 1.25 aging correction factor applied. What capacity is required?
- 3018What is the required standby duration for the secondary power supply of a typical building fire alarm system before the alarm period?
- 3019A NAC uses 14 AWG stranded copper (3.14 ohms per 1000 ft). The appliances draw 1.5 A in total and the farthest one is 300 ft from the panel. What is the voltage drop, treating the load at the end?