Question 3014 of 344 · NICET Fire Alarm Systems Level II
A 20 ft by 30 ft room has a 10 ft ceiling and will use one wall mounted strobe in the middle of the long wall. Which room size must be used to pick the candela?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3014
- C: 30 ft by 30 ft
Explanation
Wall strobe tables use square rooms. A rectangular room is rated as a square based on its longer dimension, so a 20 by 30 ft room needs the candela for a 30 by 30 ft room, unless the appliance is listed for rectangular coverage.
More questions: Submittal Preparation and System Layout
- 3015A room is 30 ft by 30 ft with one wall mounted strobe. What minimum effective intensity applies?
- 3016A 24 V battery set must support a standby load of 0.32 A for 24 h and an alarm load of 3.6 A for 5 min. Apply the 1.25 aging correction factor of NFPA 72 (2022/2025). What capacity is required?
- 3017An emergency voice/alarm communication system has a standby load of 1.1 A and an alarm load of 6.0 A. It needs 24 h standby and 15 min of alarm, with the 1.25 aging correction factor applied. What capacity is required?
- 3018What is the required standby duration for the secondary power supply of a typical building fire alarm system before the alarm period?
- 3019A NAC uses 14 AWG stranded copper (3.14 ohms per 1000 ft). The appliances draw 1.5 A in total and the farthest one is 300 ft from the panel. What is the voltage drop, treating the load at the end?
- 3020A designer starts at 20.4 V (battery end voltage) and needs at least 16.0 V at the last appliance. The NAC draws 2.0 A and uses 12 AWG solid (1.93 ohms per 1000 ft). What is the maximum one way length, with the load at the end?