Question 3017 of 344 · NICET Fire Alarm Systems Level II
An emergency voice/alarm communication system has a standby load of 1.1 A and an alarm load of 6.0 A. It needs 24 h standby and 15 min of alarm, with the 1.25 aging correction factor applied. What capacity is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3017
- C: About 34.9 Ah
Explanation
Standby: 1.1 x 24 = 26.4 Ah. Alarm: 6.0 x 15/60 = 1.5 Ah. Sum = 27.9 Ah, times 1.25 = 34.9 Ah. Voice systems use 15 min of alarm instead of the 5 min used for other systems.