Question 3018 of 344 · NICET Fire Alarm Systems Level II
What is the required standby duration for the secondary power supply of a typical building fire alarm system before the alarm period?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3018
- A: 24 hours
Explanation
Secondary power must run the system under quiescent load for 24 hours and then operate all alarm appliances for the required alarm time (5 min, or 15 min for emergency voice systems).
More questions: Submittal Preparation and System Layout
- 3019A NAC uses 14 AWG stranded copper (3.14 ohms per 1000 ft). The appliances draw 1.5 A in total and the farthest one is 300 ft from the panel. What is the voltage drop, treating the load at the end?
- 3020A designer starts at 20.4 V (battery end voltage) and needs at least 16.0 V at the last appliance. The NAC draws 2.0 A and uses 12 AWG solid (1.93 ohms per 1000 ft). What is the maximum one way length, with the load at the end?
- 3021Under the IBC, when is a manual fire alarm system required in a Group A occupancy?
- 3022Under the IBC, what happens when the fire alarm activates in a Group A occupancy with an occupant load of 1,000 or more?
- 3023Under the IBC, when is a manual fire alarm system required in a Group B occupancy?
- 3024Under the IBC, a Group E occupancy needs a manual fire alarm system at what occupant load?