Under the IBC, which fire alarm requirement applies to Group I occupancies?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3029
- A: A manual system is required in all of them
Explanation
Group I occupancies require a manual fire alarm system regardless of size, and many also need automatic smoke detection in corridors and habitable spaces. Staff notification may replace occupant notification where approved.