Question 3031 of 344 · NICET Fire Alarm Systems Level II
Under the IBC, what is the maximum area of one fire alarm zone?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3031
- C: 22,500 sq ft
Explanation
Each floor must be zoned separately, and a zone may not exceed 22,500 sq ft or 300 ft in length in any direction. This helps responders find the source quickly.
More questions: Submittal Preparation and System Layout
- 3032A single floor of a building covers 60,000 sq ft. What is the minimum number of IBC fire alarm zones for that floor?
- 3033A three story office building has floors of 12,000 sq ft each. How many IBC fire alarm zones are needed at minimum?
- 3034Under the IBC, what spare capacity must notification appliance circuits in employee work areas have when audible coverage is provided there?
- 3035Under the IBC, where must visible alarm notification appliances be provided?
- 3036Under the IMC, an air distribution system has a design capacity over what airflow before a smoke detector is required in the return air?
- 3037Under the IBC, a duct smoke detector connected to a building fire alarm system activates. What signal is required?