Question 3035 of 344 · NICET Fire Alarm Systems Level II
Under the IBC, where must visible alarm notification appliances be provided?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3035
- C: In public and common use areas
Explanation
Visible appliances are required in public use areas and common use areas, including restrooms and corridors. Private offices and work areas have special rules, and accessible sleeping units need them per the table.
More questions: Submittal Preparation and System Layout
- 3036Under the IMC, an air distribution system has a design capacity over what airflow before a smoke detector is required in the return air?
- 3037Under the IBC, a duct smoke detector connected to a building fire alarm system activates. What signal is required?
- 3038Under the IBC, how must smoke alarms in a dwelling unit with more than one alarm be connected?
- 3039Under the IBC, which feature is required in high rise buildings for occupant notification?
- 3040Which section of NFPA 101 contains the general requirements for fire detection, alarm, and communication systems?
- 3041A 500 ft long corridor has an exit at each end. Manual boxes are placed within 5 ft of each exit. How many manual boxes are needed at minimum on that floor to meet the 200 ft travel distance?