A single floor of a building covers 60,000 sq ft. What is the minimum number of IBC fire alarm zones for that floor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3032
- B: 3
Explanation
60,000 / 22,500 = 2.67, which rounds up to 3 zones. The designer must also check that no zone is longer than 300 ft in any direction, which may force more zones.