Under the IBC, a building is fully sprinklered and the occupant notification activates on sprinkler waterflow. What does the common exception allow for Group B or M?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3030
- D: Manual fire alarm boxes may be omitted
Explanation
Several occupancy sections let manual boxes be omitted in a sprinklered building when waterflow activates the notification appliances throughout. NFPA 72 still requires at least one manual box where the system supervises a sprinkler system.