Question 3036 of 344 · NICET Fire Alarm Systems Level II
Under the IMC, an air distribution system has a design capacity over what airflow before a smoke detector is required in the return air?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3036
- A: 2,000 cfm
Explanation
Smoke detectors are required in the return air of air distribution systems with a design capacity greater than 2,000 cfm. Larger systems and return risers serving multiple stories have added requirements.