What is the main purpose of a fire alarm system's sequence of operation for the AHJ?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3066
- B: To verify system responses at acceptance
Explanation
The AHJ uses the sequence of operation to confirm that each input produces the designed outputs during acceptance. It also guides future testing and changes.
More questions: Submittal Preparation and System Layout
- 3067A design places a spot smoke detector 2 ft from a supply diffuser. What should the reviewer note?
- 3068A design calls for a sidewall mounted smoke detector. What placement must the drawing show?
- 3069Which standby duration does NFPA 72 require for the secondary power of an emergency voice/alarm communication system in alarm?
- 3070Which equipment locations must the shop drawings show besides initiating devices and appliances?
- 3071When should fire alarm shop drawings normally be approved by the AHJ?
- 3072A heat detector listed for 25 ft spacing is installed on an 11 ft smooth ceiling. The multiplier for that height is 0.91. What is the adjusted spacing?