Question 1017 of 297 · NICET Fire Alarm Systems Level III

The sprinkler contractor proposes using the hoistway waterflow switch to initiate elevator shunt trip. The switch has a 60 second retard. What is the correct ruling?

Exactly one answer is correct.

Show solution

Correct answer to question 1017

  • B: Not acceptable, since a waterflow device used for shunt trip may not have a delay

Explanation

Shunt trip has to happen before or at the moment water is applied, so NFPA 72 prohibits time-delay devices on waterflow switches used for that function. Delayed shunt trip would let water reach energized elevator equipment.