Question 1017 of 297 · NICET Fire Alarm Systems Level III
The sprinkler contractor proposes using the hoistway waterflow switch to initiate elevator shunt trip. The switch has a 60 second retard. What is the correct ruling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1017
- B: Not acceptable, since a waterflow device used for shunt trip may not have a delay
Explanation
Shunt trip has to happen before or at the moment water is applied, so NFPA 72 prohibits time-delay devices on waterflow switches used for that function. Delayed shunt trip would let water reach energized elevator equipment.