Heat detectors are being installed to shunt trip the elevator power in a sprinklered machine room. Which installation meets NFPA 72?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1016
- A: Each is within 2 ft of a sprinkler, with a lower rating and higher sensitivity than the sprinkler
Explanation
The goal is to remove elevator power before sprinkler water is discharged onto the equipment. That only works if the heat detector operates first, so it must be close to each sprinkler and both more sensitive and lower rated than the sprinkler.
More questions: Installation
- 1017The sprinkler contractor proposes using the hoistway waterflow switch to initiate elevator shunt trip. The switch has a 60 second retard. What is the correct ruling?
- 1018A duct smoke detector is connected to the building fire alarm system to shut down an air handler. When it activates, what signal does NFPA 72 normally require it to initiate at the control unit?
- 1019What happens to doors held open by fire alarm controlled magnetic door holders when building power fails?
- 1020An access-controlled egress door is electrically locked. What must happen to it when the building fire alarm system activates?
- 1021The fire alarm control unit will be in a storage room that is not continuously occupied. What detection does NFPA 72 require at the control unit location?
- 1023What mounting height does NFPA 72 require for the operable part of a manual fire alarm box?