Question 1018 of 297 · NICET Fire Alarm Systems Level III
A duct smoke detector is connected to the building fire alarm system to shut down an air handler. When it activates, what signal does NFPA 72 normally require it to initiate at the control unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1018
- A: A supervisory signal
Explanation
Duct detectors are not a substitute for area smoke detection and sample air that may come from a large area, so their activation is annunciated as a supervisory signal rather than a building evacuation alarm. Many specifications still call for alarm, so read the approved documents, but the default code requirement is supervisory.