A duct smoke detector is connected to the building fire alarm system to shut down an air handler. When it activates, what signal does NFPA 72 normally require it to initiate at the control unit?

Exactly one answer is correct.

Show solution

Correct answer to question 1018

  • A: A supervisory signal

Explanation

Duct detectors are not a substitute for area smoke detection and sample air that may come from a large area, so their activation is annunciated as a supervisory signal rather than a building evacuation alarm. Many specifications still call for alarm, so read the approved documents, but the default code requirement is supervisory.