Question 1024 of 297 · NICET Fire Alarm Systems Level III
Where must manual fire alarm boxes be placed in relation to exits, when they are required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1024
- C: Within 5 ft of each exit doorway on each floor, with no more than 200 ft of travel to a box
Explanation
Pull stations go where occupants pass as they leave: within 5 ft of each exit doorway on every floor. Additional boxes are needed so the horizontal travel distance on the same floor to a box does not exceed 200 ft.
More questions: Installation
- 1025A lobby has a group of entrance doors whose total width exceeds 40 ft. How should manual fire alarm boxes be located?
- 1026During acceptance testing of a valve supervisory switch on an OS&Y valve, when must the off-normal supervisory signal appear?
- 1027A waterflow switch is tested by flowing water through the inspector's test connection. What performance does NFPA 72 require?
- 1028A technician reports that a vane-type waterflow switch with its retard set at maximum produced an alarm 120 seconds after the test valve was opened. What is the correct supervisory decision?
- 1029Where must wall-mounted visible notification appliances be installed?
- 1030Where wall-mounted audible-only appliances are installed, what height does NFPA 72 require?