What mounting height does NFPA 72 require for the operable part of a manual fire alarm box?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1023
- A: Not less than 42 in and not more than 48 in above the floor
Explanation
The operable part of a manual fire alarm box must be between 42 in and 48 in above floor level. This keeps it reachable for most people, including wheelchair users, while discouraging accidental operation.