Question 1029 of 297 · NICET Fire Alarm Systems Level III
Where must wall-mounted visible notification appliances be installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1029
- B: So the entire lens is between 80 in and 96 in above the floor
Explanation
NFPA 72 sets the wall mounting window for visible appliances at 80 in to 96 in to the whole lens. If the ceiling is too low to allow this, the appliance goes within 6 in of the ceiling. Ceiling mounted appliances use separate tables.
More questions: Installation
- 1030Where wall-mounted audible-only appliances are installed, what height does NFPA 72 require?
- 1031Three strobes are visible from one location in an open office. What must be confirmed during commissioning?
- 1032A strobe in a hotel guest room for a guest with hearing loss is mounted 30 in below the ceiling. What minimum intensity is required?
- 1033What signal characteristic must audible appliances in sleeping areas of a new hotel produce to wake occupants?
- 1034What portion of a new fire alarm system must be tested during initial acceptance testing?
- 1035After a change to site-specific software that is not supposed to affect most of the system, which reacceptance testing is required?