Question 1029 of 297 · NICET Fire Alarm Systems Level III

Where must wall-mounted visible notification appliances be installed?

Exactly one answer is correct.

Show solution

Correct answer to question 1029

  • B: So the entire lens is between 80 in and 96 in above the floor

Explanation

NFPA 72 sets the wall mounting window for visible appliances at 80 in to 96 in to the whole lens. If the ceiling is too low to allow this, the appliance goes within 6 in of the ceiling. Ceiling mounted appliances use separate tables.