A technician reports that a vane-type waterflow switch with its retard set at maximum produced an alarm 120 seconds after the test valve was opened. What is the correct supervisory decision?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1028
- A: Reject it, reduce the retard, and retest until the alarm is within 90 seconds
Explanation
The 90 second limit is a performance requirement for the waterflow alarm, regardless of the device type. A result of 120 seconds is a deficiency; adjust the retard and retest so the device complies before signing off.