Question 1028 of 297 · NICET Fire Alarm Systems Level III

A technician reports that a vane-type waterflow switch with its retard set at maximum produced an alarm 120 seconds after the test valve was opened. What is the correct supervisory decision?

Exactly one answer is correct.

Show solution

Correct answer to question 1028

  • A: Reject it, reduce the retard, and retest until the alarm is within 90 seconds

Explanation

The 90 second limit is a performance requirement for the waterflow alarm, regardless of the device type. A result of 120 seconds is a deficiency; adjust the retard and retest so the device complies before signing off.

Next to question ›