Question 1027 of 297 · NICET Fire Alarm Systems Level III
A waterflow switch is tested by flowing water through the inspector's test connection. What performance does NFPA 72 require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1027
- D: An alarm within 90 seconds of a flow equal to one sprinkler of the smallest orifice size
Explanation
The waterflow alarm must be initiated within 90 seconds of flow at the device when the flow equals that from a single sprinkler of the smallest orifice size. The retard setting plus the switch response must fit within that time.