Question 1025 of 297 · NICET Fire Alarm Systems Level III
A lobby has a group of entrance doors whose total width exceeds 40 ft. How should manual fire alarm boxes be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1025
- C: One within 5 ft of each side of the door group
Explanation
For grouped openings more than 40 ft wide, NFPA 72 requires a manual box within 5 ft of each side of the grouped opening. A single box in the middle would leave people at the far end without a box on their exit path.
More questions: Installation
- 1026During acceptance testing of a valve supervisory switch on an OS&Y valve, when must the off-normal supervisory signal appear?
- 1027A waterflow switch is tested by flowing water through the inspector's test connection. What performance does NFPA 72 require?
- 1028A technician reports that a vane-type waterflow switch with its retard set at maximum produced an alarm 120 seconds after the test valve was opened. What is the correct supervisory decision?
- 1029Where must wall-mounted visible notification appliances be installed?
- 1030Where wall-mounted audible-only appliances are installed, what height does NFPA 72 require?
- 1031Three strobes are visible from one location in an open office. What must be confirmed during commissioning?