During acceptance testing of a valve supervisory switch on an OS&Y valve, when must the off-normal supervisory signal appear?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1026
- B: Within two turns of the handwheel or one-fifth of the stem travel from normal
Explanation
Valve supervisory switches must signal early so a partly closed valve is caught. The limit is two revolutions of the handwheel or one-fifth of the stem travel from the normal position, and the signal must not restore until the valve is fully back in its normal position.