During acceptance testing of a valve supervisory switch on an OS&Y valve, when must the off-normal supervisory signal appear?

Exactly one answer is correct.

Show solution

Correct answer to question 1026

  • B: Within two turns of the handwheel or one-fifth of the stem travel from normal

Explanation

Valve supervisory switches must signal early so a partly closed valve is caught. The limit is two revolutions of the handwheel or one-fifth of the stem travel from the normal position, and the signal must not restore until the valve is fully back in its normal position.