Lead-acid batteries for the fire alarm system are delivered to the site. Which marking must the batteries carry?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1045
- A: The month and year of manufacture
Explanation
NFPA 72 requires batteries to be marked with the month and year of manufacture, or the date code of the manufacturer, so their age can be tracked. Installing old stock shortens service life and can fail the acceptance discharge test.