A ceiling smoke detector on the drawings lands 2 ft from a supply air diffuser. What is the minimum distance you should direct the installer to maintain?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1046
- C: 36 in from the diffuser
Explanation
NFPA 72 prohibits locating spot-type smoke detectors directly in the airstream and closer than 36 in to an air supply diffuser or return air opening. Moving air dilutes smoke and can also blow dust into the chamber, so the detector should be relocated and the drawings updated.