A spot smoke detector must be mounted on a sidewall because the ceiling is inaccessible. Where must it be placed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1047
- D: With the top of the detector within 12 in of the ceiling
Explanation
Wall-mounted spot smoke detectors go high on the wall, with the top of the detector within 12 in of the ceiling, because smoke collects there first. The 4 in to 12 in band measured to the top applies to wall-mounted heat detectors.