An installer mounts a spot heat detector on a wall. Which location complies with NFPA 72?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1048
- B: The top of the detector 4 in to 12 in below the ceiling
Explanation
Wall-mounted spot heat detectors must have the top of the detector between 4 in and 12 in below the ceiling. Hot gases form a layer at the ceiling, and a detector lower on the wall would respond late.