Question 1049 of 297 · NICET Fire Alarm Systems Level III
In a room with a peaked ceiling, where should the first row of spot smoke detectors be placed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1049
- B: Within 36 in of the peak, measured horizontally
Explanation
Smoke rises to the high point of a peaked ceiling, so detectors are located within 36 in horizontally of the peak. NFPA 72 also says they should not be placed in the very apex dead air pocket, so they sit a short distance down from the ridge.
More questions: Installation
- 1050During pretest, a technician activates a detector in Room 214 and the annunciator shows Room 241. What is the correct fix before acceptance?
- 1051Before starting a test on an existing monitored system, who must the Level III make sure is notified?
- 1052What must be done when testing of a monitored system is finished for the day?
- 1053You will witness acceptance testing of the elevator recall functions in a new building. Who should you schedule to be on site?
- 1054During acceptance testing, how do you verify ground fault monitoring on each circuit?
- 1055During acceptance testing, primary power to the control unit is disconnected. What result shows correct operation?