Question 1049 of 297 · NICET Fire Alarm Systems Level III

In a room with a peaked ceiling, where should the first row of spot smoke detectors be placed?

Exactly one answer is correct.

Show solution

Correct answer to question 1049

  • B: Within 36 in of the peak, measured horizontally

Explanation

Smoke rises to the high point of a peaked ceiling, so detectors are located within 36 in horizontally of the peak. NFPA 72 also says they should not be placed in the very apex dead air pocket, so they sit a short distance down from the ridge.