Before starting a test on an existing monitored system, who must the Level III make sure is notified?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1051
- D: Every person and facility that receives alarm, supervisory, or trouble signals, plus building occupants
Explanation
NFPA 72 requires notifying all persons and facilities that receive signals, and the occupants, before testing so a test is not treated as an emergency and a real fire is not ignored. The same parties must be notified again when testing is complete.
More questions: Installation
- 1052What must be done when testing of a monitored system is finished for the day?
- 1053You will witness acceptance testing of the elevator recall functions in a new building. Who should you schedule to be on site?
- 1054During acceptance testing, how do you verify ground fault monitoring on each circuit?
- 1055During acceptance testing, primary power to the control unit is disconnected. What result shows correct operation?
- 1056What secondary power duration does NFPA 72 require for a typical protected premises fire alarm system without voice evacuation?
- 1057For an in-building emergency voice/alarm communications system, how long must the secondary supply operate in alarm after 24 hours of standby?