Question 1052 of 297 · NICET Fire Alarm Systems Level III
What must be done when testing of a monitored system is finished for the day?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1052
- C: Notify the same parties that testing has ended and confirm the system is back to normal
Explanation
Testing notifications work both ways: at the end, everyone who was told about the test is told it is finished. The system must be restored to normal, with no bypassed points or disabled outputs left behind.
More questions: Installation
- 1053You will witness acceptance testing of the elevator recall functions in a new building. Who should you schedule to be on site?
- 1054During acceptance testing, how do you verify ground fault monitoring on each circuit?
- 1055During acceptance testing, primary power to the control unit is disconnected. What result shows correct operation?
- 1056What secondary power duration does NFPA 72 require for a typical protected premises fire alarm system without voice evacuation?
- 1057For an in-building emergency voice/alarm communications system, how long must the secondary supply operate in alarm after 24 hours of standby?
- 1058Your project specifies a listed standby generator as part of the secondary supply. Under NFPA 72, what minimum battery capacity is still needed?