Question 1050 of 297 · NICET Fire Alarm Systems Level III
During pretest, a technician activates a detector in Room 214 and the annunciator shows Room 241. What is the correct fix before acceptance?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1050
- A: Correct the program or device so the label matches the real location, then update records
Explanation
The annunciated location must identify where the device actually is, because responders use it to find the fire. Every device is verified against its custom label during pretest, and the record drawings and point list are updated with the final information.